I suspect nobody of us is eager to be hit by a lightning strike. The experience would be - in the best case - very painful. Lightning is a violent electrical discharge that turns the gas into a hot, electrically conducting channel through which an electric current suddenly releases energy in form of sound waves, visible and ultraviolet radiation, heat. The hot gas is in a state of matter known as "plasma" and the discharge path is often referred to as "plasma arc".

 

We don't need a thunderstorm to ignite a plasma arc. In electric circuit interrupters known as "circuit breakers" a plasma arc is drawn whenever a circuit is opened while the electric current is still flowing, and the job of the circuit breaker is - suprise surprise! - to break the circuit, namely to safely quench the arc by stopping the flow of electricity. 


lightning-1056419_1280.jpgLightning is a violent electrical discharge that turns the gas into a hot, electrically conducting channel through which an electric current releases energy in form of sound waves, radiation, heat.

Siemens MCCB.jpgA low voltage circuit breaker manufactured by Siemens AG. The interrupter triggers the contact separation studied below.

The development of new circuit breakers is challening due to the complex physics and the difficulty of dealing with lightning discharges in the lab. A new prototype of low voltage circuit breakers could easily blow up in your lab if the pressure build-up when the plasma is ignited is too high. Here's why numerical simulations can come into play as a valuable tool. Of course, turning to the digital version of a circuit breaker is not pain-free: simulations are rather complex (one has to account for fluid dynamics, radiation, electromagnetics, ferromagnetism, turbulence, heat transfer, geometry motion, numerics, you name it) but at least the only things that can explode in your laptop are the equation solver residuals.

 

 

Safety first

In this post we are not speaking about fancy plasma lamps but rather safety switches! They have to be robust with minimal maintenance and reliable even if not used for long time, because they need to be suddenly triggered when circumstances require it and they should be able to survive under sudden stress (short-circuits).

 

Circuit breakers are not supposed to be disposable one-time devices but they have to be able to undergo many switching operations. So a proper design shouldn't only account for reliability and safety but also lifetime.

 

And you do want to rely on your parachute even if it has been already used, don't you?

 

Why is it so hard to deal with circuit breakers?

Circuit breaker manufacturers usually face the nontrivial problem of not being able to carry out meaningful measurements in the arc chamber because - during contact opening - the flow environment is too harsh. Indeed, the flow can be as hot as 20,000 K or 30,000 K (the surface of the Sun is less then 6,000 K). Moreover the arc is created by a flowing electric current whose peak in short-circuit conditions can be high. Last but not least, the chambers where the arc burns are quite small (few cm) and the action is fast (in AC at 50 Hz, typical timescales of the arc are about tens of ms).

 

So you guys understand that no sensor can be placed where the real action is, a sensor that should satisfy all the above-mentioned requirements and by the way survive erosion/ablation caused by electric current, radiation and high temperatures [1].  

 

Scene_2_scene2_00001_gimp.pngLow voltage circuit breaker (half geometry) in Simcenter STAR-CCM+, initial position. The plasma arc is drawn between the two gray contact tips (silver), which are attached to the two electrodes (copper), the chamber being surrounded by a plastic enclosure. At low voltage, the current interruption is obtained by literally splitting the arc into several small arcs in series with the help of some metal blades known as splitter plates (iron).

Limiting the shooting-in-the-dark approach

According to the research engineer who kindly provided the geometry of this low voltage circuit breaker, designing a test for a new product needs at least one month "if everything goes smooth". In fact, you might have to come up with a new design, manufacture a number of prototypes and test them in the lab under different conditions. Even worse, new designs tend to be still based on the good (?) old trial-and-error approach. Needless to say, simulations have the advantage of allowing a more controlled and educated investigation of circuit breaker design and development. 


A realistic simulation

Simcenter STAR-CCM+ allows the use of a broad spectrum of physical models that - and I cannot emphasize this enough - can run simultaneously in the same simulation instance. In other words there is no need of cosimulating with another software, where one often has to make use of third-party tools in order to automatize the interface between the various different codes. 


The simulation below has been computed on 16 processors (it took one week without optimizing the setup) and the computed voltage difference is very close to the measured one. The animation shows the evolution of the temperature of the arc during contact opening [2]. The geometry has been provided by a known manufacturer and it corresponds to a real product.


WEG-angelo_16_mappers_res_interfOhmHeat@03550_Oscillogram.pngOscillogram of the simulation. Red: Voltage difference between the electrodes, namely one of macroscopic quantities that can be easily measured. Green: electric current applied as boundary condition.


For the ones of you who are familiar with the topic, the simulation includes the following features:

 

  • Ferromagnetism: Nonlinearity of the magnetic permeability of the splitter plates

  • An iterative Finite Element Magnetic Vector Potential solver for the electromagnetic equations (based on vectorial elements)

  • Evolution of eroded metal vapor, impacting electric conductivity and radiative emission/cooling

  • Arc-root voltage drop and surface Ohmic heating at the metal-plasma interface

  • Electrode motion (prescribed), mesh morphing and the occasional remeshing 

  • No need of cosimulation. Both Finite Volume and Finite Element solvers are invoked in the same instance of Simcenter STAR-CCM+

The animation shows the temporal development of the arc temperature (which correlates with the electrical conductivity distribution and hence the electric current). Our external partners who provided the geometry could even recognize from the animation the points that are melting and that are eroded in the real circuit breaker during a lab test. In fact, studying the points that have suffered the highest thermal stress tells you about the weaknesses of your design and give insight into possible reasons for failed current interruption. Moreover, a detailed animation can tell you how come those points are particularly under stress, therefore suggesting you a possible improvement of the design. The animation shed also some light on the interaction between the arc and the spatial orientation chosen for the splitter plates.

 

 

Enjoy the video!

 

(view in My Videos)


[1] There are in fact indirect measurement techniques but they are frequently carried out in simple/mock-up geometries in the lab, where usually the spectrum of the radiation emitted by the arc - integrated along the line of sight - is analyzed. From that, one can partially reconstruct the profiles of temperature, pressure and plasma composition, provided that some assumption about the shape of the arc can be made.
[2] This simulation has been carried out as a joint effort between Siemens PLM and the Hochschule fuer Technik Rapperswil (Switzerland). We thank in particular the help of Roman Fuchs.
Comments
Siemens Visionary

Nice blog, which shows the kind of multi-domain problems that Simcenter STAR-CCM+ electromagnetics can address!