PLCSIM safety

Hi,

 

I tried to connect PLCSIM with safety program with PS, but I failed. Is somebody done it? Because everytime when I want to download SAFETY to PLCSIM, PLCSIM is going to STOP mode and PS stop with fault(PLC is not in RUN mode).

Is it possible provide SAFETY with PLCSIM?

 

Thank you very much?

 

Majlov 

7 REPLIES

Re: PLCSIM safety

For the case no one answers (I can’t) :
I believe this you should rather ask the SIMATIC support/forums...


-----------------
Siemens Industry Software GmbH & Co. KG; Anschrift: Franz-Geuer-Str. 10, 50823 Köln;
Kommanditgesellschaft: Sitz der Gesellschaft: Köln; Registergericht: Amtsgericht Köln, HRA 28227;
Geschäftsführung und persönlich haftender Gesellschafter: Siemens Industry Software Management GmbH;
Geschäftsführer: Urban August, Daniel Trebes; Sitz der Gesellschaft: Köln; Registergericht: Amtsgericht Köln, HRB 70858

Re: PLCSIM safety

hello and good morning from Munich,

 

today, Siemens PLCSIM does not support safety plc.

 

 

Kind regards,

Benjamin Voelzke

Re: PLCSIM safety

Hi,

 

thank you very much for yours quick responses.

In PLCSIM is possible simulate safety. I tried it(see attachment).

 

Thank you.

Re: PLCSIM safety

i think in the picture is dosen't load hardware.

 

 

Kind regards,

Benjamin Voelzke

Re: PLCSIM safety

I made that PrtSc and I loaded hw..
Solution
Solution
Accepted by topic author Majlov
‎08-26-2015 04:32 AM

Re: PLCSIM safety

ok you are right.

my problem was, i write from process simulate safety signals in PLCSIM and PLCSIM stops.

PLCSIM Safety check the changes on input value.

Safety input is changed from outside. this is not allow.

 

Safety signal can only change the value via hardware inputs.

 

Kind regards,

Benjamin Voelzke

Re: PLCSIM safety

Aha..